Hello,
I have a question regarding the 2020 NEC and using bus bars per 250.94(B).
It states in 250.121(B) that the metal frame of a building or structure shall not be used as an equipment grounding conductor.
Does this mean that the bus bar in 250.94(b) shall not be bonded to the structural steel of a building. Or is the connection from the bus bar considered the grounding electrode conductor and falls under 250.68 (C)(2) where it states that the metal structural frame of a building shall be permitted to be used as a conductor?
The question arises because ANSI/TIA-607 states that structural steel can be used in place of a Telecommunications Bonding Backbone. However, since the NEC has been updated, the 250.121(B) raises the question if we tie the bus bar to building steel we are violating code.
Regards,
Chris
I have a question regarding the 2020 NEC and using bus bars per 250.94(B).
It states in 250.121(B) that the metal frame of a building or structure shall not be used as an equipment grounding conductor.
Does this mean that the bus bar in 250.94(b) shall not be bonded to the structural steel of a building. Or is the connection from the bus bar considered the grounding electrode conductor and falls under 250.68 (C)(2) where it states that the metal structural frame of a building shall be permitted to be used as a conductor?
The question arises because ANSI/TIA-607 states that structural steel can be used in place of a Telecommunications Bonding Backbone. However, since the NEC has been updated, the 250.121(B) raises the question if we tie the bus bar to building steel we are violating code.
Regards,
Chris