Chobbs
- Tampa, Florida
- ICT Project Manager and Designer
Hello,
I have a question regarding the 2020 NEC and using bus bars per 250.94(B).
It states in 250.121(B) that the metal frame of a building or structure shall not be used as an equipment grounding conductor.
Does this mean that the bus bar in 250.94(b) shall not be bonded to the structural steel of a building. Or is the connection from the bus bar considered the grounding electrode conductor and falls under 250.68 (C)(2) where it states that the metal structural frame of a building shall be permitted to be used as a conductor?
The question arises because ANSI/TIA-607 states that structural steel can be used in place of a Telecommunications Bonding Backbone. However, since the NEC has been updated, the 250.121(B) raises the question if we tie the bus bar to building steel we are violating code.
Regards,
Chris
Regards,
Chris