Bus duct VD calculation

Status
Not open for further replies.
Location
NYC
Occupation
Electrician
I'm calculating VD on a bus duct.
The run is 400ft,
At 275ft there is a meter bank another one at 350ft and lastly one at 400ft.
With the various online calculators there are 2 options , distributed load & concentrated load.
I'm thinking that I should be working of distributed load whereas others think I should be using concentrated load to the 1st set of meter banks & segmented loads after that.
This makes a big difference as VD is halved if I can use the distributed load.
Which table should I use?
 
to get the most accurate voltage drop, use the concentrated load and figure each section of bus duct individually, and add the results.
 
mcelweec

"With the various online calculators there are 2 options , distributed load & concentrated load."

Would you please post some "LINKS" or name the sites for a few of these calculators.
 
Ingenieur

Have you used this program ?

If you understand the inputs.....can you explain difference between cell B1 & B13 ?

'actual' B1 is your connected load
'upsize' B13 (B10?) is if you want future expansion
say your load is currently 1000 (actual), and it will be 1250 (upsize) in 2 years after expansion
if no expansion or increase in load is planned actual = upsize

play with it
change inputs and see how it changes the results
 
Last edited:
Ingenieur

Thanks again
I am tinkering...here is a rub. If B13 is not a table value (Standard Size), then everything collapses.

I will start with retagging a few things and adding some conditional drop downs.

May I reach out again later ?
 