Bus Duct

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Has anyone come across this or done this before?? The retorqing that is? What exactly would be retorqed? And they are saying afgter it's been in service. THat means it must be shutdown??

All busway joints shall be accessible and torqued as recommended by the manufacturer. A
recheck of torque setting shall be made by this Contractor after the busway has been in service
and subjected to varying load conditions. This Contractor shall submit a report of this recheck
to the Director upon completion.
 
AFIK, retorquing is normally done to eliminate loose connections. The IR scan will assist in identifying any loose connections that need to be addressed, An IR scan may eliminate and need to retorque.
Here is a decent read:
 
Last edited:
Has anyone come across this or done this before?? The retorqing that is? What exactly would be retorqed? And they are saying afgter it's been in service. THat means it must be shutdown??
No shutdown required. You can torque the cover plates on the coupling joints but the actual coupling fittings have shear heads on the bolts that break off when they're tightened. Unless recommended by the bus duct manufacturer IMO there is no reason to re-torque the couplings.
 
No shutdown required. You can torque the cover plates on the coupling joints but the actual coupling fittings have shear heads on the bolts that break off when they're tightened. Unless recommended by the bus duct manufacturer IMO there is no reason to re-torque the couplings.
Thanks
 
THanks so the IR has nothing to do with the retorqing? Or if you do the IR scan no need for retorqing and if so why?

An IR scan shows hot spots indicative of high/low resistance connections. If a joint under load shows up normal temperature wise it is assumed the connection is sound and there is no reason to put a wrench on it


Sent from my iPhone using Tapatalk
 
Here are a few photos. IR scans were done but they are not accepting that in lieu of retorqing.

Think this can still be retorqed live?
 

Attachments

  • Screenshot 2023-03-14 073919.jpg
    Screenshot 2023-03-14 073919.jpg
    172.1 KB · Views: 16
  • Screenshot 2023-03-14 073941.jpg
    Screenshot 2023-03-14 073941.jpg
    159.2 KB · Views: 16
Got it torqued, boss !
 

Attachments

  • 1678800332960.jpeg
    1678800332960.jpeg
    25.1 KB · Views: 11
Thanks..arent those parts live that you need to touch when torquing ?
No there are no live parts. Put a torque wrench on the nut ans turn. My bet would be that 99.9% of all connections are still good if they were properly torqued in the first place. If this bus duct has sheer head bolts that's a pretty good bet.
 