Fulthrotl
~Autocorrect is My Worst Enema.~
- E
ok, i had a plan, that did not survive contact with the AHJ.
expedited plan check, and less than an hour after taking my
money, my engineered wet ink signed drawings were smoked.
fooey.
this is all for a silly temp power panel for a project i'm wiring.
here was my plan:
mount a 100 amp 480 volt fused disconnect behind the main gear,
feed it using the 10 foot tap rule off an unused 800 amp main breaker,
with #2 thhn less than 10 feet long.
then go from the disconnect 30' in schedule 80, to a 75 kva xfmr, with
a 200 amp 3 phase 4 wire 120/208 volt panel mounted next to it.
sit the transformer up on a plastic support pad, so it's off the dirt.
put some 20 amp gfci devices in bell boxes next to the panel, and then
everyone can plug in their stuff for power and charging batteries, etc.
AHJ won't allow me to just hit the bottom of that 800 amp breaker.
requires i tap the bus above the breaker. before i do that, does anyone
know of or have used a clamp to hit the bus without drilling? i've used them
in trade shows to tap off main busbars in gear, but i've not seen anything
like that available.
i was given this other option to use the breaker.......
put in a 400 amp 3 phase fused disconnect, with reducers to 100 amp,
and feed it off the breaker with parallel 500 mcm copper.
anyone got suggestions for a solution?
fooey.
here was my plan: