I have searched my 05 NEC and can't come up with anything. Can anybody point me to the section that states the way for determining ampacities of busbars.
 
Re: Busbar Ampacity

Thats exactly what I needed. I don't know if I would have ever found it because they are not refered to as "busbars". Thanks.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: Busbar Ampacity

Please be aware that the 366.23(A) value is a maximum current density for field installed auxilliary gutters. Do not use these numbers to evaluate all bus bar installations.

Most manufacturers do not use current density to size their equipmnet, instead they rely on heat rise (and air flow) testing done by NRTL like UL. Note table 3 in the link provided by jimmac49. Also, multiple bars per phase ratings are dependent on the orientation and spacing of the bars.
 