Re: Busbar Ampacity
Please be aware that the 366.23(A) value is a maximum current density for field installed auxilliary gutters. Do not use these numbers to evaluate all bus bar installations.
Most manufacturers do not use current density to size their equipmnet, instead they rely on heat rise (and air flow) testing done by NRTL like UL. Note table 3 in the link provided by jimmac49. Also, multiple bars per phase ratings are dependent on the orientation and spacing of the bars.