I have a 2500 amp busduct breakered at 2500 amp. The room that was base building built was built so only half the busplugs could be used. The room has been filled with xformers and panels and I have to install a 480v/600 amp gear with a 150 kva trans to a 208v/500 amp gear. Since this will be leaving the busduct room to goto another room and I have no room to install a 600 amp busplug, what options do I have with the code for a tapbox off the busduct with the tap rule because I have room to install this. The local inspector told me to check it out and said I would be able to do this but I know that 1/3 rd of 2500 is about 850 which does not give me the option, am I missing something or is he testing me or does he not know what he is looking at?