According to Article 353.46, is it neccessary to use bushings when using male pvc adapters when terminating PVC to a box or enclosure?
352.46 Bushings. Where a conduit enters a box, fitting, or
other enclosure, a bushing or adapter shall be provided to
protect the wire from abrasion unless the box, fitting, or
enclosure design provides 352.46 Bushings. Where a conduit enters a box, fitting, or
other enclosure, a bushing or adapter shall be provided to
protect the wire from abrasion unless the box, fitting, or
enclosure design provides equivalent protection..
In my opinion yes unless the inspector feels that a typical MA provides equivalent protection.
I think many MAs have very sharp edges compared to a bushing.
300.4(G) is your answer. Just out of curiosity the title of your post says PVC and you referenced the section for HDPE:?
Pete
Sorry Pete, my mistake, if we are installing PVC with conductors smaller than #4 example 1/2"to 1".
Is it still required that we install a bushing on the male PVC connector?
Wow ! That opened a whole box of worms for me.
I have always let 300.4(G) be my guide for all conduits. Odd that we have ***.46 for RGS and IMC and PVC but not for EMT.
Are we saying a 1/2" RGS, or PVC conduit with MA needs a bushing but a 1/2" EMT with a connector does not ?
Apparently so. As an inspector I have never thought much about it unless it was 4awg or larger. Wonder if I should be:?
You bring a good point about the EMT connectors. A half-sharp pocket knife ran around the interior edge on a PVC MA will get rid of the sharp edge and then it would be just as good as any EMT connector I have came across.
Pete
I agree and require bushings for PVC MA's.
Chris
.....bushings or adaptors are required........ PVC MA=male adapter.
.....bushings or adaptors are required........ PVC MA=male adapter.
A bushing or adapter shall be provided to protect the wire from abrasion.......
A male adapter that has a sharp edge does not protect the conductors from abrasion IMHO.
Chris
Interesting.
I am not saying you are wrong but if we do read it that way when would a bushing for PVC conduit be required by this section?
According to Article 353.46, is it neccessary to use bushings when using male pvc adapters when terminating PVC to a box or enclosure?
In my opinion yes unless the inspector feels that a typical MA provides equivalent protection.
I think many MAs have very sharp edges compared to a bushing.
I agree and require bushings for PVC MA's.
Chris
Sorry Pete, my mistake, if we are installing PVC with conductors smaller than #4 example 1/2"to 1".
Is it still required that we install a bushing on the male PVC connector?
Yep. I use a solid metal bushing to pull the conductors, the pull string/rope can cut into the male PVC adapter easily and damage it or the conductors on the pull, and then replace it with a cheapo plastic one for inspection.