I was ask to help out on a large wire pull , before we stared the pull I notice that there was no 
Bell end or bushing installed on the ends of the PVC .I ask the Forman about it and I was told
They were not needed on PVC. Article 300.4 G says where # 4 or larger is installed in a raceway
A identified fitting shall be installed on the raceway To protect the conductor . My question is a
fitting required on PVC conduit that contains #4 and larger conductors? (The conduit were stubs
Up out of a concrete floor in switchgear )
	
		
			
		
		
	
				