Buss Bar Spacing
Re: Buss Bar Spacing
thanks, however I have already been to that location
I need to know how far apart the Busses need to be in a for only a 400 Amp 480VAC main load, and total clearance
thanks for your help
Robert
I am not sure I understand what you are looking for, but to me the question sounds like a manufacturer?s design issue. There is no related code requirement. (Don?s citation relates to Motor Control Centers; my interpretation of your question is that you talking about the service panel). What I mean is that you will not be able to measure the spacing on an existing configuration, compare the spacing to a table in the NEC, and pass judgement on compliance. Neither will you find an NEC table that tells you how to construct new buswork for, let us say, a network vault. Can you clarify the intent of your question?
I have an application were we are installing (2) 3 Pole 480VAC 400 Amp breakers in a free standing enclosure that will wire to buss bars for a service connection
they have asked us to provide (4) 1/4" x 2" x 8" buss bar for incoming power
Are you able to list the equipment? Or will it be field evaluated? How can you make sure the proper support is used for short circuits? All service equipment has to be listed.