Looking back at the OL, I do not see the CTs for the mains. Can I assume they are in the xfmr? Secondly, what is the operating procedure for taking a feeder breaker out of service? Is the load tied to the xfer bus and served from the middle breaker or is the feeder load tied to the xfer bus and then fed from another feeder breaker? If the middle breaker is used then, you should be able to set up two bus diff zones. The CT from the middle breaker will need to be wired to both bus diff relays with an Enable/Disable switch that turns off the middle breaker CT input to the relay that is not switched to the middle breaker. This would even allow the middle breaker to be sourced from one xfmr while supplying load from the other bus (via xfer bus).