I have a couple of installations with meter stacks that have a 2000 and 1600 amp Main breaker, but than have feeder bussing with 1200 amp bussing/meter branches and 800 amp amp bussing/meter branches
Regardless of what the manufacturer says are permissible configurations, and these being feeder busing/busways with branch taps/OCPDS to go to apartments, how does the feeder busway ampacity comply with 368.17 when it has an OCPD larger (2000 or 1600 amp) than the busway ampacity 1200 amp/800 amp?
Even looking at TAP rules, it appears to be tapping a tap.
Any thoughts from the brain bank?
Thanks
Regardless of what the manufacturer says are permissible configurations, and these being feeder busing/busways with branch taps/OCPDS to go to apartments, how does the feeder busway ampacity comply with 368.17 when it has an OCPD larger (2000 or 1600 amp) than the busway ampacity 1200 amp/800 amp?
Even looking at TAP rules, it appears to be tapping a tap.
Any thoughts from the brain bank?