Where in tarnation (in the NEC) is the 80% breaker loading language??? We all know it, and therefore never need to refer back to it and therefore dummies like me forget where it is!!!
The client says that (4) 200HP pumps could run consecutively and there are other loads on the bus too. Obviously, the pumps will have to be controlled to start separately, but thats another matter.georgestolz said:You seriously have a 1200A continuous load?
Trust me... these are continuous!haskindm said:Remember that a continuous load is a load that lasts for three-hours or more. If the pumps cycle on and off according to demand, they are not continuous. Equipment controlled by a thermostat is usually not considered continuous. Other than commercial lighting: many, many loads (if not most) are non-continuous.