busman
- Northern Virginia
- Master Electrician / Electrical Engineer
I missed the grounded secondary also.Apparently I was wrong!
Ron
Mark
Ron
Thank you! At least for the 2020 NEC, it's 250.30(A)(5) Exception 3.250.30(A)(4) Exception 3
I typically run 18AWG for 24 volt stuff like that see Table 11(A) for Inherently Limited Power Source Overcurrent Protection is Not RequiredThank you! At least for the 2020 NEC, it's 250.30(A)(5) Exception 3.
So that answers the OP's questions (1) and (2): for a voluntarily grounded Class 1, 2, or 3 transformer secondary of at most 1000VA, the GEC may be omitted per the above, and the system bonding jumper can just be sized as 250.30(A)(1) Exception 3, generally just the EGC of the circuit supplying the transformer.
As to question (3) on OCPD, there's nothing directly in Article 240 that lets you omit it, but 240.3 does refer you to Article 725, which can amend Article 240. I expect the allowance is in Article 725 somewhere, although it may only apply to Class 2 and Class 3 sources. Any pointers?
Cheers, Wayne
details details detailsBut 250.20(A) allows it to be a grounded system, and the schematic posted shows a grounded secondary.
250.30(A)(1) Exception 3 then provides relief on the System Bonding Jumper size in this application. Does anything provide relief for a GEC connection for such an installation?
Cheers, Wayne
I hinted at that in post 17, 251.121 Exception permits a wire type branch circuit equipment ground to be the GEC.However if you leave it an ungrounded system as most are, I don't see anything that says a grounding electrode system and grounding electrode conductor is not required.
For ungrounded SDSs, 250.30(B)(1) says "A grounding electrode conductor . . . shall be used . . . as specified in 250.30(A)(5) or (6), as applicable." And 230.30(A)(5) has Exception 3 for "a system that supplies a Class 1, Class 2, or Class 3 circuit and is derived from a transformer rated not more than 1000 volt-amperes." So the Exception applies to ungrounded SDSs, by direct reference.However if you leave it an ungrounded system as most are, I don't see anything that says a grounding electrode system and grounding electrode conductor is not required.
Well gee, you have raised an interesting question for sure. But yet we know that the typical ungrounded 24 volt control secondary never has a GES. Is this an oversight in the code that has never been caught? It seems odd that it is clear for grounded control circuits derived from an xformer but not for the more typical ungrounded control circuit xformer. Gonna need some research for sure.details details details
250.30(A)(5) Exception 3 addresses the GEC.
See the previous post. : - )Gonna need some research for sure.
Wayne, I did see it, but I'm try to make the leap that you suggest. Help me here.See the previous post. : - )
Cheers, Wayne
I think it has to do with it being a class 1,2, or 3 transformer but I'm not sure.Well gee, you have raised an interesting question for sure. But yet we know that the typical ungrounded 24 volt control secondary never has a GES. Is this an oversight in the code that has never been caught? It seems odd that it is clear for grounded control circuits derived from an xformer but not for the more typical ungrounded control circuit xformer. Gonna need some research for sure.
To oversimplify, 250.30(B)(1) says "do it like 250.30(A)(5) or (6)." And 250.30(A)(5) has the exception we are expecting.Wayne, I did see it, but I'm try to make the leap that you suggest. Help me here.
And no ground required - simple innit......................Very much simpler for me - batteries. They have lasted four years so far.
There's got to be a twist!I don't hear no buzzers and bells. I play by sense of smell.![]()
Well, it seems you may be correct. Kind of convoluted but I guess this is what gives us the allowance for no GES in the situation we are discussing.To oversimplify, 250.30(B)(1) says "do it like 250.30(A)(5) or (6)." And 250.30(A)(5) has the exception we are expecting.
Cheers, Wayne