By the way

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Cutler Hammer is, Afaik, the only manufacturer who has come out with a combination unit (breaker & afci receptacle) that is listed to satisfy 210.12(A)((3). Not sure what the advantage would be but it is here. Remember this production is sold as a pair (CB and it's partnered afci) not any breaker will work.
(3) A listed supplemental arc protection circuit breaker
with a listed outlet branch-circuit type arc-fault
circuit interrupter installed at the first outlet box on the
branch circuit where all of the following conditions are
met:
a. The branch-circuit wiring shall be continuous from
the branch-circuit overcurrent device to the outlet
branch-circuit arc-fault circuit interrupter.
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the first
outlet shall not exceed 15.2 m (50 ft) for a 14 AWG
conductor or 21.3 m (70 ft) for a 12 AWG conductor.
c. The first outlet box in the branch circuit shall be
marked to indicate that it is the first outlet of the
circuit.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
This is just part of the long standing AFCI fight between breaker and device manufactures. It was a bone tossed to the device manufacturers by breaker manufacturers.

The breaker manufacturers "stacked" the vote at the technical session that adopted the 2017 NEC to keep 210.12(A)(4)(d) in the code as part of this same fight. There is not even a standard to create the breaker required by that rule. The evidence shows that for the size and length of wire specified in (4) that the standard breaker provides sufficient protection for the branch circuit conductors and without the reference to this non-existent device, the breaker manufacturers fear that they would lose sales to the device manufactures. (by "stacked" I mean that there were almost twice as many NFPA members that voted on the motion on this issue as on any other motion)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Don, how can they market this. It doesn't seem likely that this will cost less then the afci breaker alone so in what case would this be worthwhile. Obviously the other manufacturers have not seen it as a worthwhile endeavor-- yet anyway
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
It might come in handy if you have an existing circuit breaker panel completely loaded twin breakers?
CH twin size breakers are an odd duck, for me anyway, but if you have to replace one of those with a new, that won’t help there. Question arises now with can the CB alone be used on existing circuits or does it always need to be paired. Thinking the device will always need the CB, but can the CB be used by itself in a non AFCI situation.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Cutler Hammer is, Afaik, the only manufacturer who has come out with a combination unit (breaker & afci receptacle) that is listed to satisfy 210.12(A)((3). Not sure what the advantage would be but it is here. Remember this production is sold as a pair (CB and it's partnered afci) not any breaker will work.

This product is to comply with 210.12(A)4)-not (A)(3). Take a look here: http://productspec.ul.com/details.php?code=nec&edition=2017&section=210.12(A)(4)&ccn=AWDT
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Thanks Texie.... I juust was wondering about the difference and whether the eaton engineer was talking about (A)(3) or (4)
 

kwired

Electron manager
Location
NE Nebraska
It might come in handy if you have an existing circuit breaker panel completely loaded twin breakers?
But the breaker and the outlet device need to be listed to be used together as a combination. Those old twin breakers may not be part of the combination. Don't know enough about them to say for certain.

The fact that Eaton is (presumably) the first one to come up with such combination of products isn't too surprising though. Eaton does own what used to be Cooper devices don't they?

Schneider and Siemens aren't making receptacle devices, and GE's power distribution products division was taken over by ABB. Eaton the only player with products made for both ends of this combination AFAIK.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I'm surprised Leviton doesn't have a listed combo since they now have panels.
 

norcal

Senior Member
CH twin size breakers are an odd duck, for me anyway, but if you have to replace one of those with a new, that won’t help there. Question arises now with can the CB alone be used on existing circuits or does it always need to be paired. Thinking the device will always need the CB, but can the CB be used by itself in a non AFCI situation.

Are you talking about the C-H type CH twins? It pretty limited where they can be used, and a huge installed base of that they were not even listed to be used in them.

The photo shows the limited positions on the bottom of the interior where twins are allowed. If they flop around on the rail where they supposed to clip on they do not belong.


URL=https://s197.photobucket.com/user/RFM959/media/IMG_0254_zps3075530f.jpg.html]
IMG_0254_zps3075530f.jpg
[/URL]
 

peter d

Senior Member
Location
New England
This is just part of the long standing AFCI fight between breaker and device manufactures.

Right, but now Eaton makes (or should I say has purchased manufacturers that make) both breakers and devices, hence why Eaton (via its now unnamed subsidiaries Cutler Hammer and Eagle Wiring Devices) make such a combination.
 

Mgraw

Senior Member
Location
Opelousas, Louisiana
Occupation
Electrician
Cutler Hammer is, Afaik, the only manufacturer who has come out with a combination unit (breaker & afci receptacle) that is listed to satisfy 210.12(A)((3). Not sure what the advantage would be but it is here. Remember this production is sold as a pair (CB and it's partnered afci) not any breaker will work.

I believe the idea behind this is to allow localized reset instead of at the panel.
 