C channel support indoor enclosed circuit breaker

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have plans that have indoor 208/120V three phase 225A enclosed circuit breaker transformer secondary that is mounted on C channel support max ten feet from the transformer.


Designer is asking me if he can mount on support C channel. I see it as design issue but not sure. Is C channel support mounting not in compliance or violation of NEC 2014 code?
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Maybe the 10’ is in reference to 240.21(CC)(2)? Why would mounting this enclosure on c channel be a design issue? Proper working clearances around enclosure to comply with 110.26?
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Maybe the 10’ is in reference to 240.21(CC)(2)? Why would mounting this enclosure on c channel be a design issue? Proper working clearances around enclosure to comply with 110.26?

Yes 240.21(C). Dont see anything on plans and Working space can be achieved without C channel support here.
 

JGinIndy

Senior Member
Location
Indiana
Occupation
Retired Electrician currently County Inspector
Not to be a “ Johnny come lately “ but is this about mounting a transformer on a strut trapeze?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
The OP is confusing but I think he wants to know if he can mount the CB on the transformer support. If that is what he wants to do, I can't see any major problem with doing so if he can do so and still meet all the requirements for working space, etc.
 
The OP is confusing but I think he wants to know if he can mount the CB on the transformer support. If that is what he wants to do, I can't see any major problem with doing so if he can do so and still meet all the requirements for working space, etc.
Seems to me he is just asking if c channel can be used as the structure to mount a circuit breaker enclosure to.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Yes I read it and just confused why mounting electrical equipment on C channel or strut would be questioned that’s all.

Thats also explained in post #1. I am confused why designer would ask plan reviewer if he wanted to do it and so wanted to follow up here see if its any NEC 2014 not code compliance or violation
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Think about it:. Have you ever seen any code article that says anything about mounting materials or sizes, i.e. no wood, minimum gauge steel, minimum size bolts, etc????

Actually.......... 110.13(A) in a roundabout way? Sorry not trying to hopelessly lengthen this thread.🥱
 