kwired
Electron manager
- NE Nebraska
- EC
I never seen where he said it was a GEC, but I have asked and haven't had an answer either.Yes, correct, reviewing the OP I see that is the application, so 250.64(C) applies. So as long as the splice is really in "the" GEC, and can't instead be construed as being in a bonding jumper (e.g. bonding jumper to GEC), then the OP needs an "irreversible compression-type connector(s) listed as grounding and bonding equipment". In which case either the Blackburn 54725 needs to shown to be listed under UL 467, or it needs to be changed out for a different splice that is.
Cheers, Wayne