Brewcrew8
Member
- Location
- Wisconsin USA
We are installing a 3000A 480/277A Service onto a building. There is a 4/0 ground ring ran around the Transformer and Ct Cabinet pad and then to the Main disconnect. We are bringing that into the main disconnect outside for the service. I was under the assumption that we would run the 4/0 ground ring into the C.T. Cabinets as well... The inspector told us he wants a jumper from the neutral bus in the CT Cabinet to the Frame of the C.T. cabinet. That means we are using the 10 - 750MCM AL neutrals that go from the C.T. cabinet to the Service disconnect. Those 10 are bonded by the main bonding jumper to the 4/0 ground ring. Thoughts on why you would bond cabinet vs directly grounding it to the ground ring?