hello all wise and knowing of the electrical code!!!!
easy questions I believe......Class 1 Division 2
first.....am I reading section 501.120(B)(2) that a general purpose dry type transformer with a 3R enclosure would be allowable?
would that also include mounting a non enclosed transformer in a Nema12 enclosure?
would a standard non-fusible disconnect mounted in a standard Nema12 enclosure need to comply with 501.115(B)(1) or 501.115(B)(2)?
thanks,
bob