We have a run of cable tray with sets of 500KCM RHH / RHW-2 copper conductors. We used NEC Table 310.20 which gave us an ampacity of 496A per conductor at 75 degree C.
These conductors are terminated in an AL/CU 90 degree C lug (the lug will accept a range of conductors up to 750KCM). The lugs are in a Square D Switchboard.
We understand that NEC 110.14 calls for the Table 310.16 conductor ampacity to be used at terminations inside equipment (only 380A for 500KCM).
The question is: Can we use the Table 310.16 ampacity of 750KCM copper (475A) at the termination, even though we are only terminating 500KCM?
Thanks.