Did you see where the Square D paper said: there is no UL Listed protective device rated with terminations greater than 75C?
i hear you but in my case all protective devices are all connected to a small bus detail that is design for the field installed cable terminations.
 

Attachments

  • IMG_7189.jpg
    IMG_7189.jpg
    45.9 KB · Views: 0

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
i hear you but in my case all protective devices are all connected to a small bus detail that is design for the field installed cable terminations.
Those appear to be simple lug landing pads which would be considered as part of the overall 'device termination' and therefore are part of its temperature rating.
 