inspector 102

Senior Member
Location
Northern Indiana
I can not seem to find the refence that feeders to a load side panel are required to be part of a cable assembly or placed in conduit. Had one guy want to run SE with a grounding conductor placed along side of cable with zip ties. Can't find code section to refence violation. Please help and thanks.
 
inspector 102 said:
That got me looking in the right location, but I think 250.134 (B) was more the language I was looking for. Thanks for the right guidance.

Your welcome, Both sections basically say the same thing.

You are right that section 250.134(B) is specific to EGC.

Chris
 