Cable conduit and fittings in C2D2

bng

New User
Location
Switzerland
Occupation
Development Engineer
Hi everyone,
I'm looking for the requirement for fittings that can be used in Class 2 Division 2.

What I found so far is
Cable conduit with UL 1660 can be used in C2D2
e.g ABB PMA CUS

What I cannot find or identify is the requirment for the fittings
Would UL 1696 or UL 514B fitting sufficient for C2D2?

Thanks!

Best regards,
Bng
 
If you are asking about conduit bodies used in a Class II, Division 2 location they are only required to be dust tight. Most manufacturers show their conduit bodies with a gasketed cover as being in compliance with UL 50E. That is the standard for dust tight enclosures.
 