ricomichigan
Member
- Location
- South Carolina
I have a 480V panel with 40kA fault current available.  I have several 20A circuit breakers in this panel with #12 wire going to my loads.  An electrical inspector has informed me that according to NEC 110.10, my wire is not protected against a fault.  His reasoning is that a fault could occur on the load side of the 20A breaker and the 20A breaker (open time of 1 cycle) will let through enough fault current to damage the insulation on the wire.  I have seen the fault current ratings of insulated wire and they are low (#12 is rated for 2768A for 1 cycle).  I have had a circuit breaker manufacturer's representative tell me that since the circuit breaker is UL 489 listed that the wire will not be damaged.  Has anyone dealt with this issue before?
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		 
 
		