Cable Guard a Wireway?

Status
Not open for further replies.

310 BLAZE IT

Senior Member
Location
NJ
I am routing single insulated USE-2 conductors through this on a roof as a permanent wiring method in lieu of caddy blocks and conduit. Do I consider this a non-metallic wireway or just a guard? I think this meets the definition of 'or equivalent' under 300.5(D)(4). Do I need to consider a percentage of fill in this guard or derate for multiple conductors? I can't find anywhere that this is required.


1629232500811.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
That is not approved as approved raceway for permanent use. Also 300.5 is for underground installations.
 