Where can I find the required or minimum distance between Deltec tie-downs for DLO cable 500MCM in a ladder type cable tray? The manufacture specs aren't very specific and the NEC dosn't mention it at all.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
See: NEC 392.30 Securing and Supporting.B)
(B) Cables and Conductors.
NEMA Standards Publication VE 2-2013
Cable Tray Installation Guidelines
Section 4 INSTALLATION OF CABLE
 