Cable in Tray

ISpud

Member
Location
Prudhoe Bay, AK
Occupation
Electrical QC Inspector
Where can I find the required or minimum distance between Deltec tie-downs for DLO cable 500MCM in a ladder type cable tray? The manufacture specs aren't very specific and the NEC dosn't mention it at all.
 
See: NEC 392.30 Securing and Supporting.B)
(B) Cables and Conductors.
NEMA Standards Publication VE 2-2013
Cable Tray Installation Guidelines
Section 4 INSTALLATION OF CABLE
 

Attachments