Good Day
We had a cable that has been exposed to a fire. Visibly the jacket seems to be scorched but the damage does not seem to be that bad. Of course we need to test to be sure or we can replace also because it was a FIRE. We did do an IR test at 5kV and the results are as follows:
Generator 12kV Cable L1-G 3.78Gohm
L2-G 4.16Gohm
L3-G 4.36Gohm
2 min test L1-L2 92.9Gohm
2 min test L1-L3 54.3Gohm
2 min test L2-L3 39.4Gohm
I know that Gohm is typically ok but NETA recommends at 2.5kV the min resistance should be 5Gohm. Also I was concerned about the variances between phases >50%. Was considering to do a HIPOT since we do not have a VLF tester but not sure voltage to test - waiting on feedback from manufacturer. Any guiudance on the results thus far? Do you recommend a HIPOT on such an old cable?
Regards
L2-G 4.16Gohm
L3-G 4.36Gohm
Regards