This can't be legal, but I am not sure how yet.
I have a large service entrance, fed with 10 sets of 750MCM aluminum cable. Each 750MCM cable ends in a Buss KFM 750MCM Cable limiter.
The switchgear consists of six bolted pressure switches. There are no main fuses, other than those cable limiters.
Loads downstream include MLO panels, automatic transfer switches, and other items without any overcurrent protection.
Am I correct in my belief that these 750 MCM Cable limiters are inadequate as the only OCP in the service entrance?
I understand the "six throws of the hand" rule, but was it really meant to indicate six unfused switches?
I have a large service entrance, fed with 10 sets of 750MCM aluminum cable. Each 750MCM cable ends in a Buss KFM 750MCM Cable limiter.
The switchgear consists of six bolted pressure switches. There are no main fuses, other than those cable limiters.
Loads downstream include MLO panels, automatic transfer switches, and other items without any overcurrent protection.
Am I correct in my belief that these 750 MCM Cable limiters are inadequate as the only OCP in the service entrance?
I understand the "six throws of the hand" rule, but was it really meant to indicate six unfused switches?