B belango99 Member May 2, 2007 #1 Hi, Can anyone help me in knowing current carrying capacity of cable lugs(eg. 10, 16, 25, 35, 50 Sq.mm etc.). along with Technical Spec. Rdgs, Elango.B
Hi, Can anyone help me in knowing current carrying capacity of cable lugs(eg. 10, 16, 25, 35, 50 Sq.mm etc.). along with Technical Spec. Rdgs, Elango.B
Pierre C Belarge Senior Member Location Westchester County, New York May 2, 2007 #2 Your best bet is to go to the website of the manufacturer of the particular lugs and seach there. If you cannot find what you are looking for, email them and ask your question to one of the techs.
Your best bet is to go to the website of the manufacturer of the particular lugs and seach there. If you cannot find what you are looking for, email them and ask your question to one of the techs.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 2, 2007 #3 Per UL Guide ZMVV all copper only wire terminations have an ampacity rating equal to the 90?C ampacity rating of the condcuctor. Don
Per UL Guide ZMVV all copper only wire terminations have an ampacity rating equal to the 90?C ampacity rating of the condcuctor. Don