Guys
In NEC section 300.50(B) it states
Protection from Damage. Conductors emerging from
the ground shall be enclosed in listed raceways. Raceways
installed on poles shall be of rigid metal conduit, intermediate metal conduit, PVC Schedule 80, or equivalent, extending
from the minimum cover depth specified in Table 300.50 to a
point 2.5 m (8 ft) above finished grade. Conductors entering a
building shall be protected by an approved enclosure or raceway
from the minimum cover depth to the point of entrance.
Where direct-buried conductors, raceways, or cables
are subject to movement by settlement or frost, they shall
be installed to prevent damage to the enclosed conductors
or to the equipment connected to the raceways. Metallic
enclosures shall be grounded.
Now I have been applying this to my MV cables now I am in a discussion with my contractor who reads the code as this section only covers individual single conductors, is he correct
In NEC section 300.50(B) it states
Protection from Damage. Conductors emerging from
the ground shall be enclosed in listed raceways. Raceways
installed on poles shall be of rigid metal conduit, intermediate metal conduit, PVC Schedule 80, or equivalent, extending
from the minimum cover depth specified in Table 300.50 to a
point 2.5 m (8 ft) above finished grade. Conductors entering a
building shall be protected by an approved enclosure or raceway
from the minimum cover depth to the point of entrance.
Where direct-buried conductors, raceways, or cables
are subject to movement by settlement or frost, they shall
be installed to prevent damage to the enclosed conductors
or to the equipment connected to the raceways. Metallic
enclosures shall be grounded.
Now I have been applying this to my MV cables now I am in a discussion with my contractor who reads the code as this section only covers individual single conductors, is he correct