In NEC section 300.5(D)(1) it states that
Emerging from Grade. Direct-buried conductors emerging from grade shall be protected by enclosures or raceways extending from the minimum cover
distance below grade required by 300.5(A) to a point at
least 2.5 m (8 ft) above finished grade. In no case shall the
protection be required to exceed 450 mm (18 in.) below
finished grade.
My question is on the protection above grade I maintain that if cable tray is used the cable tray mujst be covered front and back if the back is accessable am I correct in this assumption.
Triniboy