Discussion on how mathematically to adjust a given cable R value at a known cable operating temperature of 60C or 75C or 90C and current ambient temperature of say 30C >>>>>>>>> and adjust that R value to another ambient temperature either up or down.
NEC Chapter 9 tables 8 & 9 give us Rdc & Rac values at 75C and the formulas to move these R values to a new operating temperature either up or down.
These tables do not state anything in regards to the ambient temperature where these R values are valid.
My assumption here is the ambient is 30C since the 600V wire ampacity tables are all developed at 30C.
I have reached out to three wire manufacturers and after 2 months I still have no answer.
SKM users have a pulldown window where they can adjust the ambient for either a single circuit or the entire one-line but they do not address how they are making the adjustment internally in the program.
Southwire’s “Power Cable Manual” provides Rdc values at 25C and more generic formulas for moving from say 25 to 60, 75, or 90C.
AL : R2 = R1( (228 + T2) / (228 + T1) )
CU : R2 = R1( (234 + T2) / (234 + T1) )
Again, there is no discussion on how to address ambient temperature.
Back to the NEC, which has some generic multipliers for ampacity adjustment at different ambient temps, but I cannot find anything relating to an R adjustment for changing ambient temperatures.
Any help is appreciated.
NEC Chapter 9 tables 8 & 9 give us Rdc & Rac values at 75C and the formulas to move these R values to a new operating temperature either up or down.
These tables do not state anything in regards to the ambient temperature where these R values are valid.
My assumption here is the ambient is 30C since the 600V wire ampacity tables are all developed at 30C.
I have reached out to three wire manufacturers and after 2 months I still have no answer.
SKM users have a pulldown window where they can adjust the ambient for either a single circuit or the entire one-line but they do not address how they are making the adjustment internally in the program.
Southwire’s “Power Cable Manual” provides Rdc values at 25C and more generic formulas for moving from say 25 to 60, 75, or 90C.
AL : R2 = R1( (228 + T2) / (228 + T1) )
CU : R2 = R1( (234 + T2) / (234 + T1) )
Again, there is no discussion on how to address ambient temperature.
Back to the NEC, which has some generic multipliers for ampacity adjustment at different ambient temps, but I cannot find anything relating to an R adjustment for changing ambient temperatures.
Any help is appreciated.