IMO Kent’s suggestion is exactly right unless you are in a jurisdiction where approved ≡ listed or labeled. [The symbol “≡” means “identically equal”]. As I noted in my first response “There ain’t no such animal.” For the record though, also IMO, his suggestion should be correct in every jurisdiction.
In any cable with a “gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core,” the real issue is “…minimizing the entrance of gases or vapors and preventing propagation of flame into the cable core.” Note “minimize” the entrance and “prevent” the propagation of flame. Technically, the originating Division doesn’t matter.
ANY cable with a TC, PLTC, or ITC rating (along with any other it may have) has a “gas/vaportight continuous sheath” according to UL. (UL does not determine whether it is or isn’t “capable of transmitting gases or vapors through the cable core.”)
Therefore plugging up the end of the cable relatively well is all you should reasonably need to do.