Isaiah
- Baton Rouge
- Electrical Inspector
On 13.8kV incoming feeder they tied the cable shielding together with #6 AWG and took it (back through the ZCT) to the ground bus within the switchgear. The inspector says it needs to be #2/0 instead of #6 because that’s the size of the EGC routed with the phase conductors. Not sure why this needs to be so big since the shield is not designed to carry a large fault in the first place.