Cable shielding grounding

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
On 13.8kV incoming feeder they tied the cable shielding together with #6 AWG and took it (back through the ZCT) to the ground bus within the switchgear. The inspector says it needs to be #2/0 instead of #6 because that’s the size of the EGC routed with the phase conductors. Not sure why this needs to be so big since the shield is not designed to carry a large fault in the first place.


Sent from my iPhone using Tapatalk
 

JoeStillman

Senior Member
Location
West Chester, PA
I agree with you. The shield is not intended to carry any ground fault at all. It can, but only for a moment before it burns up. It is exactly because it DOESN"T have capacity to carry a ground fault that you have to run an equipment ground with the MV cables in the first place.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I agree with you. The shield is not intended to carry any ground fault at all. It can, but only for a moment before it burns up. It is exactly because it DOESN"T have capacity to carry a ground fault that you have to run an equipment ground with the MV cables in the first place.

Are there any guidelines for sizing this conductor relative to the shields? One of the guys said it could be as small as #10AWG?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are there any guidelines for sizing this conductor relative to the shields? One of the guys said it could be as small as #10AWG?


Sent from my iPhone using Tapatalk
I thought that the cable manufacturer determines the conductor size?
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I thought that the cable manufacturer determines the conductor size?

Collectively the 3 shields tied together equal #2AWG in terms of circular mil.
If the intent is to carry the fault for only a very short period, (? cycles per protective relaying) then I don’t see why it couldn’t be a #10AWG that ties the shields to ground


Sent from my iPhone using Tapatalk
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Doesn’t the footnote in the ampacity tables cover ALL conductors in a raceway?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
There doesn’t seem to any NEC guidelines on the shield ampacities etc


Sent from my iPhone using Tapatalk
I’m thinking back about 5-6 code cycles when there was a 250.4
I have no clue if it was moved or deleted.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
NEC 250.190 use the shield as equipment grounding.
(2) Shielded Cables. The metallic insulation shield encircling
the current-carrying conductors shall be permitted to be used
as an equipment grounding conductor, if it is rated for clearing
time of ground-fault current protective device operation without
damaging the metallic shield.
(3) Sizing. Equipment grounding conductors shall be sized in
accordance with Table 250.122 based on the current rating of
the fuse or the overcurrent setting of the protective relay.
If the shield is grounded both ends-at the source side and at the receiver side in order to mitigate the induced voltage- build up. In this case a circulating current will flow through the shield
This current may be calculated if we know the cable data
For instance, for 3 single core cables of 15 kV in flat arrangement 7.5" apart ,500 kcmils copper conductor XLPE insulated, copper, tape shielded, 3000 ft length, the currents
are 22.4,16,39 A. Then 10 awg it is o.k.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are these conductors in a metallic raceway? If so why would the shield need to be considered part of the EGC?
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
NEC 250.190 use the shield as equipment grounding.
(2) Shielded Cables. The metallic insulation shield encircling
the current-carrying conductors shall be permitted to be used
as an equipment grounding conductor, if it is rated for clearing
time of ground-fault current protective device operation without
damaging the metallic shield.
(3) Sizing. Equipment grounding conductors shall be sized in
accordance with Table 250.122 based on the current rating of
the fuse or the overcurrent setting of the protective relay.
If the shield is grounded both ends-at the source side and at the receiver side in order to mitigate the induced voltage- build up. In this case a circulating current will flow through the shield
This current may be calculated if we know the cable data
For instance, for 3 single core cables of 15 kV in flat arrangement 7.5" apart ,500 kcmils copper conductor XLPE insulated, copper, tape shielded, 3000 ft length, the currents
are 22.4,16,39 A. Then 10 awg it is o.k.

Yes you’re right. I have the cable shield data from okonite, I just have to verify the relay is set to trip before the shield is damaged -
thank you!


Sent from my iPhone using Tapatalk
 
Top