Cable Size for Generator 100KVA

Status
Not open for further replies.

Eduardo Maun

Member
Location
Qatar
I have existing generator with a capacity of 90KVA the cable size I used is 4x95 mm2, I decided to change 90 to 100 KVA, Can I still use the existing cable or should I upgrade the cable size?

Thank you...

May God Bless us all

best regards,
Eduardo
 

Besoeker

Senior Member
Location
UK
I have existing generator with a capacity of 90KVA the cable size I used is 4x95 mm2, I decided to change 90 to 100 KVA, Can I still use the existing cable or should I upgrade the cable size?

Thank you...

May God Bless us all

best regards,
Eduardo

A few questions......
Which country and what standards/codes apply?
What voltage is the generator?
Single core cables?
Armoured/unarmoured?
Method of installation?
 
Last edited:

Eduardo Maun

Member
Location
Qatar
Generator Cable Size

Generator Cable Size

A few questions......
Which country and what standards/codes apply? Qatar/Middle East
What voltage is the generator? 415Vac
Single core cables? 4C x 95 mm2
Armoured/unarmoured? Armoured
Method of installation? What is this?


Thank you...

God Bless...
 