I think most of us understand that. :grin:



In that case the NEC was not followed and it could lead to a hazard.

But there are sections in NEC that allow the breaker or fuse to have an ampacity greater than the conductors.



With the NEC when wiring a motor the breaker often provides only short circuit or ground fault protection of the conductors. The additional motor overload devices protect both the motor and the conductors.


Take a look at 230.90 Exception 3, it allows the over-current protection of service conductors to exceed the rating of the conductors.

Here is a picture I have posted many times, showing a fairly typical service in my area. In this one the conductors in the riser (top left heading up) are rated around 250 amps, with over-current protection of 600 amps. (six 100 amp breakers)


Dennis8.jpg

What do you call those SE flanges used where the cable enters the building? Got a link? I have not seen them before.
 