Hello, everyone! I would like to ask on things to consider in sizing cable that connects switchboard to switchgear. Any formula or sample will be much appreciated. Thank you so much.
The switchboard is 12kV and the main feeder breaker is 12kV, 2000 A, 40 kA rms.That’s a short question with a long answer.
If you use the NEC we can help.
What is the size feeder breaker to switchgear?
Have you done a load Calc? (Art 220)
NEC ampacity tables are in Art 310
Take a look at 240.100 and 240.101The switchboard is 12kV and the main feeder breaker is 12kV, 2000 A, 40 kA rms.