Hello everyone,
I have a confusing situation where we might need to increase cable size.
Initial wire size calculations were based on distance and motor amps. We are using ACS880 105A drive from ABB for a 55kW/100A motor. We have a circuit breaker on the input side of the VFD.
However ABB is using their recommended circuit breaker in their panel for this drive which is 250A for a 105A VFD. When redone the calculations, you can choose the certain circuit breaker, with same distance and motor amps the cable size jumps drastically. from 150mm to 240mm.
So why is the recommended circuit breaker is 2.5 times higher than VFD/motor rating ? Is it something to do complying with short circuit current ? They are recommending the same 250A breaker between 105A and 206A which is confusing. How does circuit breaker rating affect the cable this much when it's put in the software ?
Thanks in advance to all
I have a confusing situation where we might need to increase cable size.
Initial wire size calculations were based on distance and motor amps. We are using ACS880 105A drive from ABB for a 55kW/100A motor. We have a circuit breaker on the input side of the VFD.
However ABB is using their recommended circuit breaker in their panel for this drive which is 250A for a 105A VFD. When redone the calculations, you can choose the certain circuit breaker, with same distance and motor amps the cable size jumps drastically. from 150mm to 240mm.
So why is the recommended circuit breaker is 2.5 times higher than VFD/motor rating ? Is it something to do complying with short circuit current ? They are recommending the same 250A breaker between 105A and 206A which is confusing. How does circuit breaker rating affect the cable this much when it's put in the software ?
Thanks in advance to all