Cable tray 392.22 B 1 b calculation question

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
My journeyman’s calculation prep book has to be wrong again

The question is:

What is the minimum width of a ventilated trough cable tray needed for three 250 kcmil THWN, single copper conductors, six 500 kcmil THWN copper single conductors and three 750 kcmil XHHW compact ALUMINUM single conductors. All conductors have 600 volt insulation.

Book answer is 9 inch cable tray with book calculations showing 8.2341” inches squared needed. Table 392.22 B 1 Column 1 shows an 8” tray width to provide 8.5” squared area which is sufficient for 8.2341” squared area needed for these cables. Why does the book select an over size tray than the minimum width cable tray?
 

Attachments

  • IMG_2307.png
    IMG_2307.png
    102.4 KB · Views: 10
  • IMG_2308.jpeg
    IMG_2308.jpeg
    135.1 KB · Views: 10

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Book answer was 9” cable tray width but should have been an 8.5” width for clarification
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired


In my opinion, it was a confusion between THWN and THHW for 250 and 500 kcmil. THHW is double insulated and the PVC insulation thickness is more than for THWN.
In this case the total cables area will be 8.92 in^2.
 
Top