Re: Cable Tray and Water Lines
300.8 Installation of Conductors with Other Systems.
Raceways or cable trays containing electric conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
This has nothing to do with voltage levels. It flat out prohibits you from installing these type of things in raceways containing electric conductors.
It does not prohibit you from securing such things along the raceway. You just can't put it IN the raceway.
Of course you would probably not want steam lines along an electrical raceway since this would require you to figure out how hot that area would be and derate accordingly.
One could argue, that a cable tray with a barrier down the center is in effect two raceways, one for the electric conductors and one for non-electric stuff. I don't know how far that argument would get you with someone who was picky about things.
It is somewhat analogous to using the barrier to seperate conductors that could not normally be in the same raceway together.