- Location
- Illinois
- Occupation
- retired electrician
I have an application where I want to install control and instrument cables in a cable tray that passes through a Class II, Division 2 area. All of the circuits operate at 150 volts or less and 5 amps or less. These cables would be digital and analog control circuits from field instruments to a DCS. There would also be motor control circuits for motors that are controlled by the DCS. There would be no connections or terminations of the cables in the Class II, Division 2 area.
502.10(B)(4) appears to permit this application where PLTC cables are used, however if also references Article 725. I am not finding any direct reference to this installation in Article 725.
There is also a permission to use ITC in 502.10(B)(5) and I don't find any restrictions in Article 727.
I am trying to get away from the spacing requirements as found in 502.10(B)(6), but the engineer is saying that even the instrument and control circuits have to comply with the spacing requirement.
502.10(B)(4) appears to permit this application where PLTC cables are used, however if also references Article 725. I am not finding any direct reference to this installation in Article 725.
There is also a permission to use ITC in 502.10(B)(5) and I don't find any restrictions in Article 727.
I am trying to get away from the spacing requirements as found in 502.10(B)(6), but the engineer is saying that even the instrument and control circuits have to comply with the spacing requirement.