It appears to be a multi-conductor with 3-#1 AWG, & 1-#6 AWG Gnd.
The important issue is, what is the maximum outside diameter of the cable? That will determine conduit size. The overall cross sectional area of the multi-conductor cable cannot exceed 40% of the interior cross sectional area of the conduit.
For three current carrying conductors, there is not an ampacity derating, unless you are going to exceed the ambient temperature.