Hello All,
We need to run a 2000A 480V connection between the switchboards inside a building. Because of tight space going up from one floor to the above floor, the contractor suggests to use cable tray instead of conduit. Is it true that cable tray is more flexible than conduit? I think one of the reason is the bend radius of (5) sets of 4"C for 2000A connection.
If cable tray to be used, how do I size it? I read somewhere that 50% fill is max.
Last, is there any other concern about running cable tray, for example ground fault protection, etc.?
Thanks.
We need to run a 2000A 480V connection between the switchboards inside a building. Because of tight space going up from one floor to the above floor, the contractor suggests to use cable tray instead of conduit. Is it true that cable tray is more flexible than conduit? I think one of the reason is the bend radius of (5) sets of 4"C for 2000A connection.