Julius Right
Senior Member
- Occupation
- Electrical Engineer Power Station Physical Design Retired
In my opinion you need only 2.15*1.024” clearance between group of cables in square configuration
as per 392.80 Ampacity of Conductors. (A) Ampacity of Cables, Rated 2000 Volts or Less, in Cable Trays.
(2) Single-Conductor Cables. (d) Where single conductors are installed in a triangular or square configuration in uncovered cable trays.
In this case the ampacity will be as per 310.15(B)(20)-for 75oC rated copper conductor 600 mcm 553 A, for aluminum 440 A.
Nevertheless you have to check art.310.15 Ampacities for Conductors Rated 0–2000 Volts. (B) Tables. (5) Neutral Conductor.
as per 392.80 Ampacity of Conductors. (A) Ampacity of Cables, Rated 2000 Volts or Less, in Cable Trays.
(2) Single-Conductor Cables. (d) Where single conductors are installed in a triangular or square configuration in uncovered cable trays.
In this case the ampacity will be as per 310.15(B)(20)-for 75oC rated copper conductor 600 mcm 553 A, for aluminum 440 A.
Nevertheless you have to check art.310.15 Ampacities for Conductors Rated 0–2000 Volts. (B) Tables. (5) Neutral Conductor.