Julius Right
- Electrical Engineer Power Station Physical Design Retired
In my opinion you need only 2.15*1.024” clearance between group of cables in square configuration
as per 392.80 Ampacity of Conductors. (A) Ampacity of Cables, Rated 2000 Volts or Less, in Cable Trays.
(2) Single-Conductor Cables. (d) Where single conductors are installed in a triangular or square configuration in uncovered cable trays.
In this case the ampacity will be as per 310.15(B)(20)-for 75oC rated copper conductor 600 mcm 553 A, for aluminum 440 A.
Nevertheless you have to check art.310.15 Ampacities for Conductors Rated 0–2000 Volts. (B) Tables. (5) Neutral Conductor.