B billsims Member Location Alabama Apr 1, 2003 #1 Is it allowable to pull a 110 VAC HVAC control circuit in same tray with a 480 3 phase primary feed. [ April 01, 2003, 12:07 PM: Message edited by: billsims ]
Is it allowable to pull a 110 VAC HVAC control circuit in same tray with a 480 3 phase primary feed. [ April 01, 2003, 12:07 PM: Message edited by: billsims ]
B bphgravity Senior Member Location Florida Apr 1, 2003 #2 Re: Cable tray Go to Article 300.3(C)(1) of the 2002 NEC.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 1, 2003 #3 Re: Cable tray I think that we need to look at 725.26(B)(4) to find the answer. Don [ April 01, 2003, 05:29 PM: Message edited by: don_resqcapt19 ]
Re: Cable tray I think that we need to look at 725.26(B)(4) to find the answer. Don [ April 01, 2003, 05:29 PM: Message edited by: don_resqcapt19 ]