I?ve been looking through Articles 392 & 725 and I am wondering can signal tray cable be supported in 6? intervals as bundled 4 or 6 cables or does each individual cable require support every 6??
In horizontal runs, the tray itself is the support. In other than horizontal runs 392.8(B) stipulates the cables shall be fastened securely to transverse members of the cable tray. There are no other specifics that I'm aware of.tryinghard said:I’ve been looking through Articles 392 & 725 and I am wondering can signal tray cable be supported in 6’ intervals as bundled 4 or 6 cables or does each individual cable require support every 6’?
Smart $ said:In horizontal runs, the tray itself is the support. In other than horizontal runs 392.8(B) stipulates the cables shall be fastened securely to transverse members of the cable tray. There are no other specifics that I'm aware of....
What version of the NEC are you using? The 2005 version has has 8 uses permitted listed under 336.10. Items 1, 6, and 8 remain unchanged from previous cycle and #6 is regarding fire alrm cirucits. The only mention of being secured every 6' is within #7, which begins "In industrial establishments..." (Is this installation in an industrial establishment?) and the requirement therein is for securing Type TC-ER cable between the tray and utilization equipment.tryinghard said:Thanks; I see 392.8(B) but notice 336.10(6) Tray Cable, Installation, Uses Permitted:
?The cable shall be secured at intervals not exceeding 6??.
So getting an AHJ interpretation shouldn't be too difficult :grin:...Actually this is for a municipal and so I will also be the AHJ...
Smart $ said:What version of the NEC are you using?
Smart $ said:So getting an AHJ interpretation shouldn't be too difficult :grin: