Don,Bob,
How do you comply with 392.9(A)(2) when the Cableway has a width of less than 6"? I guess we could extrapolate a bit. The volume permitted in square inches is ~90% of the tray width. The Cableway product is 2" wide so we should be able to put 1.8 square inches of cable in the tray. Southwire's 12-2NM is 0.410" wide and 0.179" high. A single cable would have a area of 0.073 square inches. That would permit us to put 24 12-2 cables in the tray. That would be 4 wide and six deep in the Cableway. I would consider that to be "installed without maintaining spacing".
I am not convinced that Article 392 was ever envisioned to be used for applications like this. It wasn't that many code cycles ago that the use of cable tray was limited to industrial applications. Has there ever been any testing with this number of NM cables installed in this manner?
I see that 334.80, specifically says that the ampacity of NM installed in cable trays is per 392.11, so you are correct.
I wouldn't attempt to comply with 392.9(A)(2) since the Cableway isn't a ladder or ventillated trough cable tray. For the specific Cableway application, I believe I've always directed the discussion to 392.9(C).
Spacing isn't an issue until 392.11. As it applies to NM in Cableway, I believe 392.11(A)(1) is appropriate, but it doesn't mention spacing; 392.11(A)(2) is irrelevant; and 392.11(A)(3), while it mentions spacing, if it were relevant, would permit using the free air rating of conductors in the first place.