Allen I think I have learned not to comment on Florida procedures.
As for the staples that could be a staple listing issue.
As for the 9 current carrying conductors.
We are allowed to start with the 90C column of 310.16 for derating NM.
Table 310.16 lists 12 AWG @ 90c 30 amps.
Table 310.15(B)(2)(a) shows a 70% adjustment for 7-9 current carrying conductors.
30 amps x .7 = 21 amps, so we can still use a 20 amp breaker.
Move to 10 current carrying conductors and we get to 50% adjustment
30 x .5 = 15 so 12 AWG would now need to be on a 15 amp breaker.
There will be 2 current carrying conductors in most dwelling unit NMs 2 wire or 3 wire.
That said you should be able to bundle 4 NM cables as much as you want.
Move to 12 AWG MC and you can bundle much more because of an exception.